Hi Nima,
We have one site like this where the tech room and scanner room are separated by a control room (about 3m separation). We were attempting to fit a second system into an existing department and it was the only practicable configuration. It's a Siemens 1.5T scanner.
As mentioned previously, the biggest issue after installation was continuous acoustic noise in the control room due to the fans. Follow-up work was required after installation to try and attenuate the noise from the panels in the control room.
I'm sure there's a solution here that can get the tech room adjacent to the scanner room, even with the unusual requirement of access from multiple ORs. If not, I would definitely get confirmation in advance from scanner vendors that they can accommodate this, I'm sure they will have their own proximity requirements. There may be other third party applications that require connections between the rooms (e.g. fMRI projector, MR elastography acoustic drivers) that would be complicated or ruled out by this kind of set-up.
Kind regards,
Aaron
_____________________________
Dr Aaron McCann
Clinical Scientist
Radiological Imaging & Protection Service
Regional Medical Physics Service
Belfast Health & Social Care Trust
Forster Green Site
110 Saintfield Road
Belfast
Northern Ireland
BT8 6GR
Tel: 028 9504 4863
(Note: my normal office hours are Mon-Fri 8am - 4pm)
From: Intl_dxmedphys_wd_osu_list <intl_dxmedphys_wd_osu_list-bounces at lists.osu.edu> On Behalf Of Nima Kasraie via Intl_dxmedphys_wd_osu_list
Sent: 12 May 2026 01:49
To: DxMedPhys List <intl_dxmedphys_wd_osu_list at lists.osu.edu>
Subject: [Intl_DxMedPhys] How far can an MRI Eq. Rm. be?
CAUTION: This email originated from outside the Belfast Trust.
Do not click links or open attachments unless you recognise the sender and know the content is safe.
Hey folks, Here's another one for you: So they're building a new $5Billion pediatric hospital here on campus that will open in 2031 with 9 MRI magnets. But I noticed this in the plans of the interventional MRI: I have never seen
Hey folks,
Here's another one for you:
So they're building a new $5Billion pediatric hospital here on campus that will open in 2031 with 9 MRI magnets. But I noticed this in the plans of the interventional MRI:
[cid:image003.png at 01DCE2B5.BC63FE60]
I have never seen an equipment room placed so far from a Zone 4 room. Will this even work? I mean, cables thru the ceiling?? Will vendors accept this?
Thoughts?
Nima Kasraie, PhD, MSc, DABR (D), DABSNM (I)
Professor of Radiology
Medical Physics Division
Department of Radiology
5323 Harry Hines Blvd., Dallas, Texas 75390-9071
Phone: 214-648-7978
https://urldefense.com/v3/__http://www.utsouthwestern.edu/radiology__;!!KGKeukY!wbfQtd3qL3Y9PON59IJS2jd3jsz2rscvfgDwmRCdBbKdT5Mq2VuSbZ-UDu0bHdSVbFFt1MOtf4rR6YHA5VPBh_ckk37hByCgHtJX8z3LpSxqln_OfXSuWAw$ <https://urldefense.com/v3/__http:/www.utsouthwestern.edu/radiology__;!!KGKeukY!1LCv0JJrSVVY3nvtGOzuSyZFmTJw1j_m9SCe5XiHwd8BoJyTpmni4sDqcwoidI9jNx98HekfSyeyYHQ2GTQJvXVnZRM-JjUhxbfuPBEu4cpk4NacAwk4Zw$>
[cid:image004.png at 01DCE2B5.BC63FE60]
[cid:image005.png at 01DCE2B5.BC63FE60]
________________________________
UT Southwestern
Medical Center
The future of medicine, today.
This message contains information from Belfast Health And Social Care Trust which may be privileged and confidential. If you believe you are not the intended recipient any disclosure, distribution or use of the contents is prohibited. If you have received this message in error, please notify the sender immediately. This email has been scanned for the presence of computer viruses.
________________________________
This message contains information from Belfast Health And Social Care Trust which may be privileged and confidential.
If you believe you are not the intended recipient any disclosure, distribution or use of the contents is prohibited.
If you have received this message in error please notify the sender immediately.
This email has been scanned for the presence of computer viruses.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.osu.edu/pipermail/intl_dxmedphys_wd_osu_list/attachments/20260513/636f14a8/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 262884 bytes
Desc: image003.png
URL: <http://lists.osu.edu/pipermail/intl_dxmedphys_wd_osu_list/attachments/20260513/636f14a8/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 10985 bytes
Desc: image004.png
URL: <http://lists.osu.edu/pipermail/intl_dxmedphys_wd_osu_list/attachments/20260513/636f14a8/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 31503 bytes
Desc: image005.png
URL: <http://lists.osu.edu/pipermail/intl_dxmedphys_wd_osu_list/attachments/20260513/636f14a8/attachment-0002.png>
More information about the Intl_dxmedphys_wd_osu_list
mailing list