[ALERT] Outage Status Update - AHU-2 at 50%

Physics facility information facility_info at groups.asc.ohio-state.edu
Wed Jul 9 13:32:41 EDT 2014


During restart of AHU-2 a circuit breaker serving one of the two main supply fans within the unit failed and must be replaced.

FOD is currently having difficulty with the restart of AHU-2 and related exhaust fans.

Once restarted, AHU-2 will run at 50% until the replacement part is obtained and installed.

It is hoped that the part can be obtained overnight.

Occupants may notice pressure imbalances in the building and in specific labs while this non-standard operating condition is in place.

Other tasks from today's outage including the East Regional Chiller Plant load testing and the Emergency Generator load bank test were completed as planned.